I have had a kitchen refit with a wiring upgrade. My electric cooker was re-connected yesterday and I tried to cook on it but it trips out the sockets as well as itself.


Today the contractor says there is a fault with my cooker which is causing the trip out and it's not their problem.


There was nothing wrong with the cooker before and it worked perfectly.


I appreciate it's difficult for an electrician to make a hard and fast comment on this without an inspection and test but could an electrician reading this confirm if this is possible ?


Thanks

Link to comment
https://www.eastdulwichforum.co.uk/topic/106231-any-electricians-in-the-house/
Share on other sites

KidKruger Wrote:

-------------------------------------------------------

> It's obviously possible, if there's a fault with

> the cooker (or the cabling specific to the

> cooker).

> You don't need a sparky to establish that.


but as I said in the text the cooker worked perfectly before and there was no fault then

Do you know if during the refit the electrician fitted a new consumer unit just to service the kitchen or was it wired to your existing consumer unit ?

If the former then I guess that the whole unit is tripping which is also taking out the kitchen sockets linked to the same unit. Seems strange. Could be worth checking that they have fitted an appropriately rated miniature circuit breaker (MCB) for the cooker 30 amps is normal.

I certainly hope that they haven't combined the cooker and sockets on the same circuit - they should be separate.


Consumer Unit - http://www.screwfix.com/c/electrical-lighting/domestic-consumer-units/cat7230028

MCB - http://www.screwfix.com/c/electrical-lighting/mcbs/cat7230022?cm_sp=managedredirect-_-electrical-_-mcb

Thank you Uncleglen for your reply


The contractors electrician fitted the cooker whilst I was there to speak to him. I oversaw his work and all was in order with the re-connection.



You raise two important matters though.


1. The 30amp fuse


How do I visually verify the Amperage of the fuse.ie, where is the fuse for me to inspect and confirm that it is 30A ?


2. the cooker is on a upgraded and rewired system. I think it is not on a separate system otherwise why would it trip the household sockets?


Regards

ed_pete Wrote:

-------------------------------------------------------

> Do you know if during the refit the electrician

> fitted a new consumer unit just to service the

> kitchen or was it wired to your existing consumer

> unit ?

> If the former then I guess that the whole unit is

> tripping which is also taking out the kitchen

> sockets linked to the same unit. Seems strange.

> Could be worth checking that they have fitted an

> appropriately rated miniature circuit breaker

> (MCB) for the cooker 30 amps is normal.

> I certainly hope that they haven't combined the

> cooker and sockets on the same circuit - they

> should be separate.

>

> Consumer Unit -

> http://www.screwfix.com/c/electrical-lighting/dome

> stic-consumer-units/cat7230028

> MCB -

> http://www.screwfix.com/c/electrical-lighting/mcbs

> /cat7230022?cm_sp=managedredirect-_-electrical-_-m

> cb



Thank you very much for your reply ed_pete. If you don't mind I'll take what you have suggested to the foreman electrician on Monday morning.


Regards

Hi pipsky2008, sorry to hear you are having a bad experience with this.


Feel free to check out our other recommendations here:

http://www.eastdulwichforum.co.uk/forum/read.php?30,1660314


We can come by and get to the bottom of the problem for you, If you would like to give us a call to book an electrician please call us on 0207 205 2255


Kind regards,

Mike at HomeCert

pipsky2008 Wrote:

-------------------------------------------------------

> ed_pete Wrote:

> --------------------------------------------------

> -----

> > Do you know if during the refit the electrician

> > fitted a new consumer unit just to service the

> > kitchen or was it wired to your existing

> consumer

> > unit ?

> > If the former then I guess that the whole unit

> is

> > tripping which is also taking out the kitchen

> > sockets linked to the same unit. Seems strange.

>

> > Could be worth checking that they have fitted

> an

> > appropriately rated miniature circuit breaker

> > (MCB) for the cooker 30 amps is normal.

> > I certainly hope that they haven't combined the

> > cooker and sockets on the same circuit - they

> > should be separate.

> >

> > Consumer Unit -

> >

> http://www.screwfix.com/c/electrical-lighting/dome

>

> > stic-consumer-units/cat7230028

> > MCB -

> >

> http://www.screwfix.com/c/electrical-lighting/mcbs

>

> >

> /cat7230022?cm_sp=managedredirect-_-electrical-_-m

>

> > cb

>

>

> Thank you very much for your reply ed_pete. If you

> don't mind I'll take what you have suggested to

> the foreman electrician on Monday morning.

>

> Regards


By all means but bear in mind that I'm only a semi-competent amateur not a professional. As regards your question about the "30 amp fuse". "Fuses" aren't fitted any more, modern consumer units have the MCB's that I referred to but sometimes these are still referred to as a fuse. If you can find the consumer unit the ampage is normally one of the numbers on MCB. Typically lighting circuits are 10 amps or less, ring mains for sockets around 30. Just checked and our oven is on a 40amp MCB.

Seabag Wrote:

-------------------------------------------------------

> Really please, just get a proper sparky in

>

> The great/worse thing about an electric shock is;

> you can't see it coming


What you say about not being able to see an electric shock coming is true but I have put up this post to gather information to counter a contractors statement of liability rather than to do any electrical work myself.


You are entirely right to point out the dangers of D.I.Y electrical work if you are not qualified

> The contractors electrician fitted the cooker whilst I was there to speak

> to him. I oversaw his work and all was in order with the re-connection.


What do you mean "all was in order"? Did he test the cooker, and did you see him doing so? How extensive were his tests?

How has the situation changed since then? Have you tried to use some part or function of the cooker that he didn't try? Have you tried to reproduce precisely whatever testing it was he did?

Hi ianr


> The contractors electrician fitted the cooker whilst I was there to speak

> to him. I oversaw his work and all was in order with the re-connection.


By that I mean I wanted to be at home to see the cooker re-installed as my cooker has an old wiring system and I wanted to be clear about colour to colour compatibility as It is likely that I would need to uninstall the cooker myself to paint the floor under it and reinstall it again myself.


I needed to remind myself with an old to new mixed installation :


Red to Brown - live


Black to Blue - neutral


Green and yellow to green and yellow - earth


I watched while he wired this connection up, which he did. I then turned on two of the rings, which warmed up and the system did not trip in the way I have described above. I have been loaned a hotplate which I operate from a socket in the lounge which was not in operation at the time. All seemed 'in order' when he and I were present


Did he test the cooker, and did you see him doing so?


He made no tests of any kind, other than me turning on two rings


How extensive were his tests?


As above, he made no tests of any kind.


The site manager has booked an appointment for further tests of the cooker to try to ascertain where the fault lies.


I would like though to gather some knowledge to go into discussion with the contractor so as not to be palmed off.


Many thanks


Regards

Testing sounds the right thing to do. I think fuller testing at the time would have been sensible. My presumption would be that if a system -- whether kitchen electrics, computer suite, car -- seems be to working ok but then shows fault after an upgrade, there's possibly something amiss with the upgrade. Nevertheless, it could be that it's revealed a latent fault or quirk that you didn't notice before. I don't know the extent of the upgrade.


I can't offer definitive knowledge. The information I'd be wanting from the tests would be answers to questions like these. What is the trip switch cut-off setting? Is it definitely operating according to specification? Is there any specific function of the cooker that triggers the trip? What's the maximum current (Amps) drawn then? Is that typical of this or any other types of cooker, or is it a fault that's developed? Is it a transient thing -- eg a 'spike' happening only at the moment a relevant cooker switch is turned on/off or is that bit of the cooker always drawing that size current? What would the likely remedies be? Would they include changing the trip switch's cut-off setting? If it's a transient thing, would a safe temporary work-around be to simply leave the switch on and reset the trip switch?

Thanks very much ianr and ed_pete


I have noted the questions you suggest. I feel far better armed


I bumped into the foreman electrician the other day, who is still on site. He thought it could be an earth leak or that previous to the upgrade the cooker hadn't been within an RCD but that now it was.


He didn't feel it was necessary for the cooker to be within the RCD but there wasn't time to go into detail.


I'm awaiting an appointment but I am getting the feeling they hope I just go away as I'm getting the silent treatment from the contractor.


I saw this link for anyone else learning the basics of electrics like me http://www.jlmelectrical.co.uk/my-rcd-keeps-tripping/



Regards

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Latest Discussions

    • Direct link to joint statement : https://thehaguegroup.org/meetings-bogota-en/?link_id=2&can_id=2d0a0048aad3d4915e3e761ac87ffe47&source=email-pi-briefing-no-26-the-bogota-breakthrough&email_referrer=email_2819587&email_subject=pi-briefing-no-26-the-bogot_-breakthrough&&   No. 26 | The Bogotá Breakthrough “The era of impunity is over.” That was the message from Bogotá, Colombia, where governments from across the Global South and beyond took the most ambitious coordinated action since Israel’s genocidal assault on Gaza began 21 months ago. Convened by The Hague Group and co-chaired by the governments of Colombia and South Africa, the Emergency Conference on Palestine brought together 30 states for two days of intensive deliberation — and emerged with a concrete, coordinated six-point plan to restrain Israel’s war machine and uphold international law. States took up the call from their host, Colombian President and Progressive International Council Member Gustavo Petro, who had urged them to be “protagonists together.” Twelve governments signed onto the measures immediately. The rest now have a deadline: 20 September 2025, on the eve of the United Nations General Assembly. The unprecedented six measures commit states to:     Prevent military and dual use exports to Israel.     Refuse Israeli weapons transfers at their ports.     Prevent vessels carrying weapons to Israel under their national flags.     Review all public contracts to prevent public institutions and funds from supporting Israel’s illegal occupation.     Pursue justice for international crimes.     Support universal jurisdiction to hold perpetrators accountable. “We came to Bogotá to make history — and we did,” said Colombian President Gustavo Petro. “Together, we have begun the work of ending the era of impunity. These measures show that we will no longer allow international law to be treated as optional, or Palestinian life as disposable.” The measures are not symbolic. They are grounded in binding obligations under international law — including the International Court of Justice’s July 2024 advisory opinion declaring Israel’s occupation unlawful, and September 2024’s UN General Assembly Resolution ES-10/24, which gave states a 12-month deadline to act. UN Special Rapporteur on the situation of human rights in the occupied Palestinian territory Francesca Albanese called them “a momentous step forward.” “The Hague Group was born to advance international law in an era of impunity,” said South Africa’s Foreign Minister, Ronald Lamola. “The measures adopted in Bogotá show that we are serious — and that coordinated state action is possible.” The response from Washington was swift — and revealing. In a threatening statement to journalists, a US State Department spokesperson accused The Hague Group of “seeking to isolate Israel” and warned that the US would “aggressively defend our interests, our military, and our allies, including Israel, from such coordinated legal and diplomatic” actions. But instead of deterring action, the threats have only clarified the stakes. In Bogotá, states did not flinch. They acted — and they invite the world to join them. The deadline for further states to take up the measures is now two months away. And with it, the pressure is mounting for governments across the world — from Brazil to Ireland, Chile to Spain — to match words with action. As Albanese said, “the clock is now ticking for states — from Europe to the Arab world and beyond — to join them.” This is not a moment to observe. It is a moment to act. Share the Joint Statement from Bogotá and popularise the six measures. Write to your elected representative and your government and demand they sign on before 20 September. History was made in Bogotá. Now, it’s up to all of us to ensure it becomes reality, that Palestinian life is not disposable and international law is not optional. The era of impunity is coming to an end. Palestine is not alone. In solidarity, The Progressive International Secretariat  
    • Most countries charge for entry to museums and galleries, often a different rate for locals (tax payers) and foreign nationals. The National Gallery could do this, also places like the Museums in South Kensington, the British Library and other tax-funded institutions. Many cities abroad add a tourist tax to hotel bills. It means tourists help pay for public services.
    • Having just been to Co-op to redeem a 50p off Co-op members' card voucher on an item that is now 50p more than it was last week, Tesco can't come soon enough
    • Surely that depends on the amount.  It can be quite piffling.  
Home
Events
Sign In

Sign In



Or sign in with one of these services

Search
×
    Search In
×
×
  • Create New...