I have had a kitchen refit with a wiring upgrade. My electric cooker was re-connected yesterday and I tried to cook on it but it trips out the sockets as well as itself.


Today the contractor says there is a fault with my cooker which is causing the trip out and it's not their problem.


There was nothing wrong with the cooker before and it worked perfectly.


I appreciate it's difficult for an electrician to make a hard and fast comment on this without an inspection and test but could an electrician reading this confirm if this is possible ?


Thanks

Link to comment
https://www.eastdulwichforum.co.uk/topic/106231-any-electricians-in-the-house/
Share on other sites

KidKruger Wrote:

-------------------------------------------------------

> It's obviously possible, if there's a fault with

> the cooker (or the cabling specific to the

> cooker).

> You don't need a sparky to establish that.


but as I said in the text the cooker worked perfectly before and there was no fault then

Do you know if during the refit the electrician fitted a new consumer unit just to service the kitchen or was it wired to your existing consumer unit ?

If the former then I guess that the whole unit is tripping which is also taking out the kitchen sockets linked to the same unit. Seems strange. Could be worth checking that they have fitted an appropriately rated miniature circuit breaker (MCB) for the cooker 30 amps is normal.

I certainly hope that they haven't combined the cooker and sockets on the same circuit - they should be separate.


Consumer Unit - http://www.screwfix.com/c/electrical-lighting/domestic-consumer-units/cat7230028

MCB - http://www.screwfix.com/c/electrical-lighting/mcbs/cat7230022?cm_sp=managedredirect-_-electrical-_-mcb

Thank you Uncleglen for your reply


The contractors electrician fitted the cooker whilst I was there to speak to him. I oversaw his work and all was in order with the re-connection.



You raise two important matters though.


1. The 30amp fuse


How do I visually verify the Amperage of the fuse.ie, where is the fuse for me to inspect and confirm that it is 30A ?


2. the cooker is on a upgraded and rewired system. I think it is not on a separate system otherwise why would it trip the household sockets?


Regards

ed_pete Wrote:

-------------------------------------------------------

> Do you know if during the refit the electrician

> fitted a new consumer unit just to service the

> kitchen or was it wired to your existing consumer

> unit ?

> If the former then I guess that the whole unit is

> tripping which is also taking out the kitchen

> sockets linked to the same unit. Seems strange.

> Could be worth checking that they have fitted an

> appropriately rated miniature circuit breaker

> (MCB) for the cooker 30 amps is normal.

> I certainly hope that they haven't combined the

> cooker and sockets on the same circuit - they

> should be separate.

>

> Consumer Unit -

> http://www.screwfix.com/c/electrical-lighting/dome

> stic-consumer-units/cat7230028

> MCB -

> http://www.screwfix.com/c/electrical-lighting/mcbs

> /cat7230022?cm_sp=managedredirect-_-electrical-_-m

> cb



Thank you very much for your reply ed_pete. If you don't mind I'll take what you have suggested to the foreman electrician on Monday morning.


Regards

Hi pipsky2008, sorry to hear you are having a bad experience with this.


Feel free to check out our other recommendations here:

http://www.eastdulwichforum.co.uk/forum/read.php?30,1660314


We can come by and get to the bottom of the problem for you, If you would like to give us a call to book an electrician please call us on 0207 205 2255


Kind regards,

Mike at HomeCert

pipsky2008 Wrote:

-------------------------------------------------------

> ed_pete Wrote:

> --------------------------------------------------

> -----

> > Do you know if during the refit the electrician

> > fitted a new consumer unit just to service the

> > kitchen or was it wired to your existing

> consumer

> > unit ?

> > If the former then I guess that the whole unit

> is

> > tripping which is also taking out the kitchen

> > sockets linked to the same unit. Seems strange.

>

> > Could be worth checking that they have fitted

> an

> > appropriately rated miniature circuit breaker

> > (MCB) for the cooker 30 amps is normal.

> > I certainly hope that they haven't combined the

> > cooker and sockets on the same circuit - they

> > should be separate.

> >

> > Consumer Unit -

> >

> http://www.screwfix.com/c/electrical-lighting/dome

>

> > stic-consumer-units/cat7230028

> > MCB -

> >

> http://www.screwfix.com/c/electrical-lighting/mcbs

>

> >

> /cat7230022?cm_sp=managedredirect-_-electrical-_-m

>

> > cb

>

>

> Thank you very much for your reply ed_pete. If you

> don't mind I'll take what you have suggested to

> the foreman electrician on Monday morning.

>

> Regards


By all means but bear in mind that I'm only a semi-competent amateur not a professional. As regards your question about the "30 amp fuse". "Fuses" aren't fitted any more, modern consumer units have the MCB's that I referred to but sometimes these are still referred to as a fuse. If you can find the consumer unit the ampage is normally one of the numbers on MCB. Typically lighting circuits are 10 amps or less, ring mains for sockets around 30. Just checked and our oven is on a 40amp MCB.

Seabag Wrote:

-------------------------------------------------------

> Really please, just get a proper sparky in

>

> The great/worse thing about an electric shock is;

> you can't see it coming


What you say about not being able to see an electric shock coming is true but I have put up this post to gather information to counter a contractors statement of liability rather than to do any electrical work myself.


You are entirely right to point out the dangers of D.I.Y electrical work if you are not qualified

> The contractors electrician fitted the cooker whilst I was there to speak

> to him. I oversaw his work and all was in order with the re-connection.


What do you mean "all was in order"? Did he test the cooker, and did you see him doing so? How extensive were his tests?

How has the situation changed since then? Have you tried to use some part or function of the cooker that he didn't try? Have you tried to reproduce precisely whatever testing it was he did?

Hi ianr


> The contractors electrician fitted the cooker whilst I was there to speak

> to him. I oversaw his work and all was in order with the re-connection.


By that I mean I wanted to be at home to see the cooker re-installed as my cooker has an old wiring system and I wanted to be clear about colour to colour compatibility as It is likely that I would need to uninstall the cooker myself to paint the floor under it and reinstall it again myself.


I needed to remind myself with an old to new mixed installation :


Red to Brown - live


Black to Blue - neutral


Green and yellow to green and yellow - earth


I watched while he wired this connection up, which he did. I then turned on two of the rings, which warmed up and the system did not trip in the way I have described above. I have been loaned a hotplate which I operate from a socket in the lounge which was not in operation at the time. All seemed 'in order' when he and I were present


Did he test the cooker, and did you see him doing so?


He made no tests of any kind, other than me turning on two rings


How extensive were his tests?


As above, he made no tests of any kind.


The site manager has booked an appointment for further tests of the cooker to try to ascertain where the fault lies.


I would like though to gather some knowledge to go into discussion with the contractor so as not to be palmed off.


Many thanks


Regards

Testing sounds the right thing to do. I think fuller testing at the time would have been sensible. My presumption would be that if a system -- whether kitchen electrics, computer suite, car -- seems be to working ok but then shows fault after an upgrade, there's possibly something amiss with the upgrade. Nevertheless, it could be that it's revealed a latent fault or quirk that you didn't notice before. I don't know the extent of the upgrade.


I can't offer definitive knowledge. The information I'd be wanting from the tests would be answers to questions like these. What is the trip switch cut-off setting? Is it definitely operating according to specification? Is there any specific function of the cooker that triggers the trip? What's the maximum current (Amps) drawn then? Is that typical of this or any other types of cooker, or is it a fault that's developed? Is it a transient thing -- eg a 'spike' happening only at the moment a relevant cooker switch is turned on/off or is that bit of the cooker always drawing that size current? What would the likely remedies be? Would they include changing the trip switch's cut-off setting? If it's a transient thing, would a safe temporary work-around be to simply leave the switch on and reset the trip switch?

Thanks very much ianr and ed_pete


I have noted the questions you suggest. I feel far better armed


I bumped into the foreman electrician the other day, who is still on site. He thought it could be an earth leak or that previous to the upgrade the cooker hadn't been within an RCD but that now it was.


He didn't feel it was necessary for the cooker to be within the RCD but there wasn't time to go into detail.


I'm awaiting an appointment but I am getting the feeling they hope I just go away as I'm getting the silent treatment from the contractor.


I saw this link for anyone else learning the basics of electrics like me http://www.jlmelectrical.co.uk/my-rcd-keeps-tripping/



Regards

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Latest Discussions

    • My understanding is the "free event" is 100% Gala, nothing to do with the council. Obviously Gala will still make money from the food & drink that they are trying to coerce punters into buying on their social media posts. Their costs will be negligible due to already having the infrastructure in place for Gala. So Gala are trying to appear community minded by providing this "free event", but the real goal is to set a precedent for a fourth day's festival - which surely no one could possibly object to?!? - in preparation for applying (again) for two three-day festivals spread over two weekends. It's only another two days, right, and the site & equipment is already there, so why would anyone object?!? More money for the council, much more money for Gala, win-win right? But yet another week of our park taken away from us, too, and another 18,000 people trampling & littering the park, and another week of disturbance for the native birds & wildlife...
    • Meson Don Felipe on The Cut was my go to place for many years. Though it's now many years since I was there. 10-15 minute walk from the Tate. If you go can you tell me what it's like nowadays?
    • Doubt you would have got much change out of £150.00 for battery and certainly having forked out for it, best to use your car. I recently sold  my car via webuyanycar.com - very pleasant experience & was roughly what I was expecting. Pop your bangers reg jnto their website to get an idea of price - they do send e mails once a fortnight/month just as an aid for you. Easy enough to delete - don’t even have to read valuation. They literally buy any car - if you can’t get it to them, they will charge you to get it there or recommend a co that will do it for you. Must say, mine was a 2014 reg and whilst a bit suspicious, paid extra to get money into my account as needed it for next car but was assured funds had I not gone down route I took would be in my account within 5 days. I now live in the country - every time I have been back to Dulwich and surrounding area, normally get a fine for driving at wrong time or parking at  wrong time so if I drive now, park in West or East Dulwich and do everything else by public transport and walking.  Were I still to be living in ED then before I left was pondering this very issue but since I have been back regularly for health reason I no longer drive but take the train and then buses, walk or Uber. Much cheaper than running a car and had I stayed, that would have been the course I would have taken. I don’t go out everyday, have an allotment or job to go to or family so in my case, would be cheaper not to have a car.  Was truely shocked   at the cost of second hand cars…..but where I now live only has a smattering of buses so no choice but to have wheels to get from A to B etc.          
    • If you don't use the car often then suggest disconnect the battery between use by undoing the earth (negative / minus sign) cable from the battery and the battery will then last longer between use. Remember, central locking, alarm, clock, etc won't work with battery disconnected and wit ours I have to lock the doors with central locking before disconnecting battery as only have key on one door (leave bonnet open before locking doors). Hope this helps  
Home
Events
Sign In

Sign In



Or sign in with one of these services

Search
×
    Search In
×
×
  • Create New...